A colleague's nephew has emailed this science question from an assignment (A level physics?) as my colleague thinks I'm brilliant at all academic things. I can't remember any of it :lol: .

Question:

Quote:
"A new industrial consumer located 10km away from a grid supply point requires a 200kW supply. The consumer is to be supplied via aluminium overhead cables that have a cross sectional area of 100mm2 and a resistance of 0.03 x 10^-6 ohms/m. Show the reason why it is not practical to supply power to this consumer at the safer 415 volts rather than the 32kV used by calculating the current that would be needed to supply the power if the two alternative voltages (415 V and 32kV) were adopted. Assume that the ac supply is single phase."


So far I've thought:

Total resistance will be (10,000m x 0.03 x 10^-6 ohms/m)

Ohm's Law(s): P = I x V and V = I x R, so knowing V: voltage (415 or 32k), P:required power (200kw) we can get figures for current for both voltages, in two ways, i.e.

If P = I x V then I = P/V, ditto if V = I x R then I = V/R. Presumably if you put your figures for V and P in, you'll get different I: currents for the lower voltage, thus proving it's impractical?

But I don't know what what the relevance of the cross-sectional area or it being single phase AC are.

I also can't remember what the SI units are in each case: m, ohms, amps, but is the power SI unit watts?


Top
 Profile Send private message  
 
PostPosted: Wed Mar 30, 2011 21:58 
Offline
Gold Member
Gold Member

Joined: Sun Jun 27, 2004 14:47
Posts: 1659
Location: A Dark Desert Highway
About £6000


Top
 Profile Send private message  
 
PostPosted: Wed Mar 30, 2011 22:13 
Offline
Life Member
Life Member
User avatar

Joined: Sun Sep 25, 2005 21:17
Posts: 3734
Location: Dorset/Somerset border
I just had a eureka moment in the bath.

V = I x R (or I = V/R) tells us the (I) current figure that is the minimum necessary to overcome the given resistance, correct?

And in P = I x V (or I = P/V) the (I) current figure is that actually supplied by each of the suggested voltages.

So the I value from the second equation needs to be higher than that produced by the first equation, in other words there needs to be at least as much current as we get from V = I x R to overcome the resistance.

In other words, if you put figures in, I bet with 415V the current figure in Amps will be not high enough, but with 32 kilovolts it will. Hence a 415v system will be "not practical".

Still don't know why we need to know the X-sectional area of the cable or that it's AC tho'



:scratchchin:


Top
 Profile Send private message  
 
PostPosted: Wed Mar 30, 2011 22:18 
Offline
Friend of Safe Speed
Friend of Safe Speed
User avatar

Joined: Sun Sep 25, 2005 10:16
Posts: 7986
Location: Moved to London
I know where the question is going, but there is something wrong with this:
Quote:
... via aluminium overhead cables that have a cross sectional area of 100mm2 and a resistance of 0.03 x 10^-6 ohms/m.

That set of numbers seems wrong to me, and doesn't fit with the spirit of the question. I calculate the resistance of 100mm2 of alu to be 100x their figure.
edited to add: no, the question isn't clear.

JTB wrote:
Still don't know why we need to know the X-sectional area of the cable or that it's AC tho'

Yes, I think you're Right JTB. If I'm right with where I think the question is going, the X-area is fairly redundant.
The AC doesn't really matter, the RMS issues sort themselves out for this question.

_________________
Views expressed are personal opinions and are not necessarily shared by the Safe Speed campaign


Top
 Profile Send private message  
 
PostPosted: Wed Mar 30, 2011 22:30 
Offline
Life Member
Life Member

Joined: Sat Mar 27, 2004 13:50
Posts: 2643
I think the cross-sectional area has nothing to do with the power loss calculation, which is a simple matter of applying Ohm's Law.
However, it probably has a lot to do with how hot the cable gets - but that's getting a bit beyond my comfort zone.

_________________
Only when ideology, prejudice and dogma are set aside does the truth emerge - Kepler


Top
 Profile Send private message  
 
PostPosted: Wed Mar 30, 2011 22:39 
Offline
Friend of Safe Speed
Friend of Safe Speed
User avatar

Joined: Sun Sep 25, 2005 10:16
Posts: 7986
Location: Moved to London
Quote:
... via aluminium overhead cables that have a cross sectional area of 100mm2 and a resistance of 0.03 x 10^-6 ohms/m.

The latter part implies the resistance of the cable per meter (so apparently making the X-area redundant), but I now recognise that figure as the "specific resistance" (rho). :roll:
That really wasn't clear!

Anyway

R = rho * L/A = 0.03e-6 * 1 / (0.1 * 0.1) = 3e-6 ohms per meter.
For 10km = 0.03 Ohms

For 415V, the current must be 200kW/415V = 482A. Vdrop for two runs of cable (to close the circuit) = 29V
That means only 386V at the outlet.
The cable would dissipate/waste 14KW - that's a lot of power loss!

For 32KV, the current must be 200kW/415V = 6.25A. Vdrop for two runs of cable (to close the circuit) = 0.375V
The cable would waste 2.3W - not at all significant.

_________________
Views expressed are personal opinions and are not necessarily shared by the Safe Speed campaign


Top
 Profile Send private message  
 
PostPosted: Wed Mar 30, 2011 22:58 
Offline
Life Member
Life Member
User avatar

Joined: Thu Jun 22, 2006 13:54
Posts: 1711
Location: NW Kent
Steve wrote:
R = rho * L/A = 0.03e-6 * 1 / (0.1 * 0.1) = 3e-6 ohms per meter.
For 10km = 0.03 Ohms



Or

R = rho * L/A = 0.03e-6 * 1 / (0.1 * 0.1) = 3e-4 ohms per meter.
For 10km = 3 Ohms

:)

_________________
Driving fast is for a particular time and place, I can do it I just only do it occasionally because I am a gentleman.
- James May


Top
 Profile Send private message  
 
PostPosted: Wed Mar 30, 2011 23:02 
Offline
Friend of Safe Speed
Friend of Safe Speed
User avatar

Joined: Sun Sep 25, 2005 10:16
Posts: 7986
Location: Moved to London
Toltec wrote:
Steve wrote:
R = rho * L/A = 0.03e-6 * 1 / (0.1 * 0.1) = 3e-6 ohms per meter.
For 10km = 0.03 Ohms



Or

R = rho * L/A = 0.03e-6 * 1 / (0.1 * 0.1) = 3e-4 ohms per meter.
For 10km = 3 Ohms

:)

I think I have to disagree with you Toltec.

Not only have you multiplied the 'mantissa' (?) by 100, you also adjusted the 'exponent' by that factor too.

_________________
Views expressed are personal opinions and are not necessarily shared by the Safe Speed campaign


Top
 Profile Send private message  
 
PostPosted: Wed Mar 30, 2011 23:40 
Offline
Life Member
Life Member

Joined: Sat Mar 27, 2004 13:50
Posts: 2643
Steve wrote:
...but I now recognise that figure as the "specific resistance" (rho). :roll:


Yes, I'd forgotten completely about that - it's been a very long time :cry:

_________________
Only when ideology, prejudice and dogma are set aside does the truth emerge - Kepler


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 01:34 
Offline
User
User avatar

Joined: Tue Feb 15, 2005 00:15
Posts: 5232
Location: Windermere
IIRC, the West Coast Main Line uses aluminium TUBE rather than cable to increase surface area, and reduce resistance and weight.

Is that any help? :roll:

_________________
Time to take responsibility for our actions.. and don't be afraid of speaking out!


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 02:10 
Offline
Friend of Safe Speed
Friend of Safe Speed
User avatar

Joined: Sun Sep 25, 2005 10:16
Posts: 7986
Location: Moved to London
Ernest Marsh wrote:
IIRC, the West Coast Main Line uses aluminium TUBE rather than cable to increase surface area, and reduce resistance and weight.

Is that any help? :roll:

This is a very good point, one I hadn't considered. I suspect the questioner didn't consider that either, so I'll let myself off :D

Yes - in the real world, it is a bit silly having an AC power cable as large as 100mm2, the "skin effect" would render much of the cross-sectional area useless.
Realistically, one could triple (finger in air estimate) the DC resistance of such a cable, as well as the voltage drops and power losses.

All this is assuming "100mm2" means '(100 millimetres) squared' as opposed to '100 square millimetres'. If the latter is the correct interpretation then my earlier maths is waaaaay out, and the 200kw wouldn't be merely impractical - it would actually be outright impossible!

_________________
Views expressed are personal opinions and are not necessarily shared by the Safe Speed campaign


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 02:42 
Offline
User
User avatar

Joined: Tue Feb 15, 2005 00:15
Posts: 5232
Location: Windermere
Steve wrote:
so I'll let myself off :D

I'm not so sure whether to give the question setter 100 lines or you, young Steven! :listenup: :whip: :hehe:

100mm² :rotfl: :doh: :shocked:

I can't help think that he (the question setter) didn't think this question through. A similar thing happened to me in a question which involved the shutter speed and frame rate in a movie projector.

I gave the right answer - which I got wrong, because the question failed to take into account factors such as the pausing of each frame!

_________________
Time to take responsibility for our actions.. and don't be afraid of speaking out!


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 03:13 
Offline
User
User avatar

Joined: Tue Feb 15, 2005 00:15
Posts: 5232
Location: Windermere
I have given this some thought - and the best answer would be for them to buy a big diesel powered industrial generator, and generate on site - supplemented by a 125 meter wind turbine if planning conditions allow, for periods when the plant is on shut down or maintenance! :lol:

This of course would all come to nought if any NIMBYs called the planning decision in for a public enquiry, as the legal fees would outweigh the benefits! :whome:

They could of course be in a position to supply back to the grid - thus sidestepping the environmental levy! :angel:

_________________
Time to take responsibility for our actions.. and don't be afraid of speaking out!


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 08:05 
Offline
Supporter
Supporter
User avatar

Joined: Thu Oct 16, 2008 13:45
Posts: 4042
Location: Near Buxton, Derbyshire
Steve wrote:
All this is assuming "100mm2" means '(100 millimetres) squared' as opposed to '100 square millimetres'. If the latter is the correct interpretation then my earlier maths is waaaaay out, and the 200kw wouldn't be merely impractical - it would actually be outright impossible!


Bit late on this since I had an early night last night but my two pennorth is that even if the 100mm^2 means what it says - a cable 1.27cm in diameter - than the proposal is ludicrous at 415 and quite workable at 32kV. With a cable that size at 50Hz I think skin effect is negligible.

If the X-section are is 100mm^2 -(10mm * 10mm) that is 10e-4 m^2
So R = pL/A = .03 10E-6 * 10e4 /10e-4 = .03 10e (-6 + 4 + 4) = .03 e2 = 3 ohms
Because it is single phase the loop resistance is twice that, 6 ohms.

200kW at 415volts is almost 500Amps and ohms law shows voltage drop of 3000volts. Greater than the sourse voltage!
At 32 kv you are looking at just over 6amps for a 40volt drop. Quite manageable and rather in line with what I remember from my time at the CEGB.

The units for resistivity are ohm metre not ohms per metre so the question is very misleading.

_________________
When I see an adult on a bicycle, I do not despair for the future of the human race. H.G. Wells
When I see a youth in a motor car I do d.c.brown


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 08:20 
Offline
Life Member
Life Member
User avatar

Joined: Sun Sep 25, 2005 21:17
Posts: 3734
Location: Dorset/Somerset border
dcbwhaley wrote:
So R = pL/A


Thanks all :clap:


What does pL stand for in that equation? Just so I'm clear?


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 08:28 
Offline
Supporter
Supporter
User avatar

Joined: Thu Oct 16, 2008 13:45
Posts: 4042
Location: Near Buxton, Derbyshire
Johnnytheboy wrote:
dcbwhaley wrote:
So R = pL/A


Thanks all :clap:


What does pL stand for in that equation? Just so I'm clear?


p should be Greek rho, the symbol for resistivity - aka specific resistance - which is measured in ohms * meters (not ohms/meter as in the question)
L is the length of the cable in metres
A is the cross sectional area of the cable in square metres

_________________
When I see an adult on a bicycle, I do not despair for the future of the human race. H.G. Wells
When I see a youth in a motor car I do d.c.brown


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 09:34 
Offline
Gold Member
Gold Member
User avatar

Joined: Wed Dec 08, 2004 14:26
Posts: 4364
Location: Hampshire/Wiltshire Border
Yes, I would agree with DCB's analysis. The issue is voltage drop at the high current required at the lower voltage level. It's easy to forget that there are two cable lengths - line and return. Skin effect is negligible at 50Hz. :)

_________________
Malcolm W.
The views expressed in this post are personal opinions and do not represent the views of Safespeed.


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 10:17 
Offline
Supporter
Supporter
User avatar

Joined: Thu Oct 16, 2008 13:45
Posts: 4042
Location: Near Buxton, Derbyshire
malcolmw wrote:
Skin effect is negligible at 50Hz. :)


In copper the "skin depth" at 50 hz is just under a centimeter. That means that there is no significant skin effect for cables up to 2cm diameter. However if there is any harmonic component then the skin depth for that will be less.
Skin effect is taken into account in designing large busbars and switchgear, and equipment designed for 50Hz working has to derated if it is used at 400Hz

_________________
When I see an adult on a bicycle, I do not despair for the future of the human race. H.G. Wells
When I see a youth in a motor car I do d.c.brown


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 11:10 
Offline
Gold Member
Gold Member
User avatar

Joined: Wed Dec 08, 2004 14:26
Posts: 4364
Location: Hampshire/Wiltshire Border
DCB is quite correct. Switchgear and bussbars tend to be made from solid copper parts. Litz construction can be used on large cables to mitigate skin effect.

_________________
Malcolm W.
The views expressed in this post are personal opinions and do not represent the views of Safespeed.


Top
 Profile Send private message  
 
PostPosted: Thu Mar 31, 2011 12:26 
Offline
Friend of Safe Speed
Friend of Safe Speed
User avatar

Joined: Sun Sep 25, 2005 10:16
Posts: 7986
Location: Moved to London
Ernest Marsh wrote:
I'm not so sure whether to give the question setter 100 lines or you, young Steven! :listenup: :whip: :hehe:

Both it seems!

dcbwhaley wrote:
Steve wrote:
All this is assuming "100mm2" means '(100 millimetres) squared' as opposed to '100 square millimetres'. If the latter is the correct interpretation then my earlier maths is waaaaay out, and the 200kw wouldn't be merely impractical - it would actually be outright impossible!


Bit late on this since I had an early night last night but my two pennorth is that even if the 100mm^2 means what it says - a cable 1.27cm in diameter ...

:doh: (aimed at myself, not you DCB)
What is the recognised written short-hand notation for '(100 millimetres) squared' and '100 square millimetres' ?

_________________
Views expressed are personal opinions and are not necessarily shared by the Safe Speed campaign


Top
 Profile Send private message  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 27 posts ]  Go to page 1, 2  Next

All times are UTC [ DST ]


Who is online

Users browsing this forum: No registered users and 268 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You can post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Group
[ Time : 0.114s | 12 Queries | GZIP : Off ]